Solving the Tesla Powerwall frequency problem

TLDR: Useful if Tesla Powerwall frequency shifting during outages is affecting appliances like clocks, furnaces, uninterruptible power sources (UPS), etc. Want to skip right to fixing the Tesla Powerwall frequency problem? Click here.

In February 2018, we installed a Tesla Powerwall 2.0 on our Vermont home. We get around thirty outages a year, and for the last 5 years this device has provided us with a reliable automatic backup electricity source capable of running our home through outages of up to two days. (Read more about my experience with our Tesla Powerwall here.)

Whenever there was a lengthy outage, I noticed that my old-fashioned digital clocks would run a little fast. I’d reset them to the correct time and didn’t think much about it.

Until one day…

Houston, we have a problem

Earlier this year, I reluctantly dismantled our 38-year-old solar hot water and space heating system, and replaced it with a gas boiler. (One of the system’s large, expensive solar storage tanks had sprung a leak, and I would have had to replace all three tanks. Our solar collectors were still working flawlessly, but I worried that they might not last much longer.)

The gas boiler, a high efficiency Alpine condensing boiler, was installed to heat a new stainless steel domestic hot water tank and the two existing radiant floor heating systems. After dealing with the inevitable teething troubles, the system was working well.

Until we had a power outage while the boiler was running.

Passing the small utility room that contains the heating system, I noticed a red glow that was definitely not normal. Going in, I saw that the boiler’s touch screen display had turned red. The boiler had shut down with a “hard lockout”. Looking up the displayed error message “Fault 23” told me that the boiler was unhappy with the Tesla Powerwall’s power.

This was not OK. First, the boiler would not operate during a power outage. Furthermore, it would not turn on automatically once utility power returned. That’s because you have to manually reset the hard lockout using the boiler’s touch screen.

So if we left our home for a few days and a power outage occurred during that time, the boiler would not operate until someone entered our home and reset it. Having our plumbing freeze and plants die while we were away was not acceptable.

Diagnosing the problem

It wasn’t hard to figure out what was happening, once I remembered the previously ignored clue that some of our clocks ran fast when using Powerwall power. These clocks are the old-fashioned kind that keep time based on the national electric utility frequency of 60 hertz (Hz). Clearly, the Powerwall must be providing backup power at a higher frequency.

To my surprise, a quick Google search told me that Powerwalls supply power at 66 Hz when they are at full or close to full charge! My furnace was shutting down because, unlike the rest of my appliances, it would not operate correctly at 66 Hz. But why would Powerwalls do this?

Well, it turns out that many Powerwalls are used as storage for photovoltaic (PV) solar panels. PV systems also use an inverter, like the one in a Powerwall, to generate household power. And when the house’s electrical needs are being met with the Powerwall charged to or near full, there’s nowhere for additional solar-generated electricity to go. So the Powerwall is designed to switch to 66 Hz under these conditions. PV inverters, like my furnace, see the frequency out of the normal spec and shut down. The Powerwall supplies the home until it has spare capacity to be recharged by the solar panels, and then drops its frequency down to 60 Hz. Until then, the solar inverter (and my furnace) will shut down.

Ok, so I understand the problem and the reason Powerwalls are designed this way. But I don’t have PV panels, and I want my furnace to work when there’s a power outage! What could I do?

Fixing the Tesla Powerwall frequency problem – option 1

Luckily, as you might expect, I wasn’t the first customer to have this problem. More Googling indicated that I could call Tesla and ask them to remotely update my Powerwall to reduce the frequency of power it provided under high charge conditions.

So I did. After a long hold time for Tesla Powerwall Support [(888) 765-2489], I spoke with a friendly technician, Manny. He confirmed that Tesla will make this change and placed an order for my system. Manny told me the change usually took 3 – 5 business days, and he would get back to me when they did it.

I waited. After nine days, I called back to get an update, and Andrea told me the queue was currently running 10 – 15 business days. So I waited some more.

Sixteen days after I’d spoken with Manny, he emailed me that Tesla had made the change. Great! Now, I wanted to test to see if the fix worked.

Testing that Tesla’s update worked

I didn’t want to wait until a power outage occurred while my furnace was running. So I decided to manually switch our home to Powerwall power.

I hadn’t done this before, so I investigated my Powerwall installation. It’s mounted on an external wall, so it’s easy to see the components. Please note that there are several ways to install Powerwalls — don’t assume that your configuration will be the same as mine. Here’s a photo, with the components labeled, of my setup.

Tesla Powerwall frequency Grid power flows through my utility meter through the gateway to the Powerwall disconnect, which is hooked up to both the Powerwall and my main home breaker panel.

For my setup, to switch our home to Powerwall power manually you simply have to open the gateway box and turn off the grid disconnect switch.

Tesla Powerwall frequency

After flipping the grid disconnect switch, I went inside and turned up a thermostat so our boiler would fire up. Success! The Alpine now worked happily on Powerwall backup power!

I don’t own a multimeter that includes frequency measurement, but I found another way to discover the frequency that my Powerwall now generates. By logging in via your gateway’s Wi-Fi network, it’s possible to view the operating frequency of your Powerwall. These instructions provide a guide. I discovered that my Powerwall’s output is now between 62.1 – 62.3 Hz. Apparently, that’s close enough to 60 Hz to keep the boiler running.

Fixing the Tesla Powerwall frequency problem – option 2

Although I solved my boiler problem, that doesn’t mean other appliances or devices are immune from Tesla’s frequency switching technology. If that turns out to be the case for you, there is another option that should work, though you’d have to pay for it.

The trick is to use an online aka double-conversion uninterruptible power supply (UPS) to power the troublesome device. (Offline/Standby, Line-Interactive, and Automatic Voltage Regulation types of UPS don’t change the frequency of the power supplied.) An online UPS charges a battery that runs an inverter providing 120 volts, 60 Hz power independent of incoming power quality. When grid power fails, this type of UPS has no transfer time. Plug the problematic device into an online UPS that has enough volt-amp (VA) capacity and you’re all set. Note that the backup time such units provide is irrelevant since they will still be receiving power from the Powerwall.

The only drawback to this solution is the expense. An online UPS costs more than the other types. The least expensive unit I could find via a quick search, the Maruson 1000VA Online Double-Conversion UPS, costs almost $500.

Conclusions

Once again, I’m very happy with my Tesla Powerwall. It would be nice if an installer or owner could make this frequency change, rather than waiting for two weeks for Tesla to do it. But at least there was a fix that only cost some time for research and a couple of phone calls, and my boiler power problem is resolved.

I hope this article will help anyone else who runs into the same problem. Please share your experiences and suggestions in the comments below.

 

How to solve the infuriating HTTP error when uploading images or videos to WordPress

Here’s a foolproof method to fix the dreaded HTTP error seen when attempting to upload images, videos, or other accepted file types to the WordPress Media Library.

One of the most frustrating aspects of using the popular WordPress platform is running into this error when attempting to upload media. If you’ve never experienced this, you’re lucky! I run into this problem on ~1% of my image uploads and have wasted a lot of time and energy trying to resolve it.

solve HTTP error uploading WordPress
I’m not alone. The two million plus hits returned by a quick Google search for the cause of this problem make it abundantly clear that this problem is common, and that there is neither a simple explanation why it occurs nor a single solution that prevents it from happening. Here is a summary of some of the “solutions” that have been proposed:

  • Reduce image size
  • Increase PHP memory
  • Disable mod_security
  • Disable plugins
  • Change php.ini and /or .htaccess settings
  • Install a newer version of php
  • Disable image optimization
  • Change upload folder permissions

I’m not denying that these approaches work under some circumstances, and if you are consistently unable to successfully upload images to the WordPress media library you should probably investigate them. But be prepared for a lot of messing about with no guarantee of success. (At least, that was my experience.)

So, here’s a solution that works (note: except for websites hosted at wordpress.com, because plugins cannot be added to such sites).

How to avoid an HTTP error when uploading media to WordPress
Begin with these three one-time-only steps:

  1. Obtain and set up an FTP program so you can transfer files to your WordPress host. If you didn’t understand that sentence, don’t worry: here’s a beginner’s guide to obtaining an FTP program and using FTP to transfer files to and from your WordPress site.
  2. Install the Add From Server plugin and activate it. If you don’t know how to install a WordPress plugin, consult this clear beginner’s guide.
  3. From your WordPress Dashboard, check Settings > Add From Server. The default settings [User Access Control All users with the ability to upload files] & [Root Directory Do not lock browsing to a specific directory] should be fine for general use.

Once you’ve completed the above steps, you can upload media to your WordPress library as follows:

  1. Run your FTP program and navigate to the appropriate folder to upload your media. There are a couple of possibilities here. For a default WordPress installation, the appropriate folder will be your Uploads folder, i.e. (..[NameOfYourSite]/wp-content/Uploads/).
  2. If, however, you have the WordPress Dashboard Settings > Media option Organize my uploads into month- and year-based folders checked, you will probably want to upload your media into a subfolder of Uploads that has the form [CurrentFourDigitYear/CurrentTwoDigitMonth/], for example ..[NameOfYourSite]/wp-content/Uploads/2017/07/. Note that if this is your first upload for the current month, the folder won’t exist and you’ll need to create it using the FTP program.
  3. From your WordPress Dashboard, go to Media > Add From Server.
    solve HTTP error uploading WordPress
  4. Use the navigation links at the top of the Add From Server screen to navigate to the same folder you chose in step 1 or 2.solve HTTP error uploading WordPress
  5. Click the checkmark box (or boxes) next to the media you wish to add. Then scroll to the bottom of the page. There’s an option to set the imported date to the current date and time [default] or the file’s creation date and time. I think the default is most appropriate, but feel free to choose the alternative. Click the Import button and voila! Your selection(s) will be added to your WordPress Media Library!

That’s it! Although this description of the process is long, once you’ve set up your FTP program the five steps above take very little time to complete. I hope this has been helpful, and welcome your comments below!